Sparkingchip:
The requirement for RCD protection didn’t go from nothing to everything in one go, there was a gradual change driven by regs and guidance to contractors, mainly from the NICEIC.
Perhaps someone would like to add dates:
- No RCD protection required for any sockets.
- RCD protection required for sockets likely to be used outdoors, so the developers started fitting a socket with a built in RCD in the back of the garage or similar.
- All ground floor sockets deemed likely to be used to supply outdoor equipment, so the ground floor socket ring has a RCBO.
- All sockets require RCD protection.
In many cases the cooker circuit with a single socket has slipped through the net and still does not have RCD protection. In rented homes the landlords will generally do the bare minimum amount of upgrading, so anything coded C3 will still be exactly the same in five years time as it is now. There’s no reason to use an EICR to apply unnecessary pressure on a landlord to upgrade an installation, but not spending any money on an installation that is over thirty years old is hardly the act of a professional landlord.
There is actually a high probability of the cooker socket being used for outdoor equipment if any work is done in a home, because if the builders, kitchen fitters, electrician, etc turn the socket circuit off whilst work is carried out the cooker switch socket will be used for the equipment they are using outdoors, an occurrence I see regularly.
So is the coding for any socket without RCD protection C2 unless it is in a flat on the first floor or above?
Andy Betteridge
John Peckham:
Chris
If the 50m extension lead is "reasonably foreseeable " then a C2 would be appropriate. How would you code the non-compliance?
davezawadi:
Hm, this is getting difficult because it is being suggested that a change in the regulations in a fairly minor way makes an installation go from satisfactory to unsatisfactory. In the same way we could say that every installation now needs a new CU. If the regulations can wield such power then the people making them need to be accountable for the huge cost, and need to provide evidence of increased safety of a significant nature, such as guaranteeing a reduction of deaths from electric shock or fires by 10% immediately, not just a bit of hand waving and a general statement of "increased safety". It seems we are in a bad place when "back covering" is more important than good regulation. Ok I could change the cooker switch / socket for £50 quid, but that is not the point. I could fit a 30mA RCD to the whole installation but fall foul of those who would say this is unsafe because a trip removes all the lights. I could fit an RCBO to the cooker circuit, but because the oven element is old it trips when the oven is hot. Where does this retrospective chain end, because I think that it does not. I repeat my remarks about speed limits above, is this really where you want to be? I shall stick with C3 and a note of what to do for safety. If it is ignored this is not my problem and it would be very difficult to prove that it was, unless the customer could not read, and then they could not pay me by cheque (nothing else accepted!).
Sparkingchip:
The rental laws lack clarity, the government doesn’t actually seem to say if an EICR with C3 observations on it is acceptable or not.
If there are EICRs with issues coded C3 will there have to be a lot of belated improvements and upgrades to electrical installation later this year?
Andy Betteridge
(4) Where a report under sub-paragraph (3)(a) indicates that a private landlord is or is potentially in breach of the duty under sub-paragraph (1)(a) and the report requires the private landlord to undertake further investigative or remedial work, the private landlord must ensure that further investigative or remedial work is carried out by a qualified person