Help with installation / diagram

Former Community Member
Former Community Member
Hi,


I am after some help with a heated windows installation / diagram - grateful for any input.

Unfortunately, the company supplying the installion went bust and I have been left with a system that doesn't  work (incorrectly designed).

We had a local electrician do the first fix wiring based on the diagrams but he says what has been sent won't work in it's current state and he doesn't have the relevant expertise to adjust it.

We live in a rural area and electricians are not that common especially for something as complex as this.

Rather than post up the diagrams and go into too much detail initially, I just wanted to know if this is a place to ask for advice and if not could anyone point me in the right direction. e.g contact details for an electrical engineer.


Thanks.
Parents
  • Lack of CPC to windows is consistent with transformers being intended to make it SELV, but any voltage over 50 would break that. The use of 3 phase +N bus-bar suggests the breakers were supposed to be on primary side, with lots of single phase transformers, and is not really consistent with the drawings.


Reply
  • Lack of CPC to windows is consistent with transformers being intended to make it SELV, but any voltage over 50 would break that. The use of 3 phase +N bus-bar suggests the breakers were supposed to be on primary side, with lots of single phase transformers, and is not really consistent with the drawings.