Can we state that because the 5x test trips at less than 40ms it complies with fault protection, or does the 30mA disconnection time also have to comply?
lyledunn:
How many times was it subject to test? Many times I have got +200ms on x1 or even no trip on first assault. Hit the test button a few times and then different results. If you have already done this then given your results, there is nothing to be concerned about.
disconnection will occur within the required time for a L-PE fault of negligible impedance.
I had missed those last two words, so as the 5x tests are all under 40ms I don't think we have a problem.
Many thanks again