RB1981:
It's actually tested with 14A on one side (a moderate overload) and 6A on the other. I think for one hour.
I hope that there are not many others, who think that a twin socket is rated for 26A.
AJJewsbury:
I hope that there are not many others, who think that a twin socket is rated for 26A.
Depends on the manufacturer. Some exceed BS 1363 minimum requirements. For instance I think MK state that their sockets are rated 13A per outlet - i.e. up to 26A per twin.
Still only 13 A total according to their literature.
AJJewsbury:
Still only 13 A total according to their literature.
This one https://www.mkelectric.com/Documents/English/EN%20MK%20Technical%20Specifications/WD%20general%20tech.pdf
seems to say "Current rating: 13A per socket outlet (except 3 gang which is 13 amp in total)" - maybe they've gone downhill since that was published.
Given that it is perfectly possible to insert two plugs, each fused at 13 A, it seems odd that if the rating for the pair is only 13 A