mapj1:
Inside equipment, because it can be type tested for approval (think of a megger-like test) you can show that an alternative arrangement is possible.
For example on a PCB with primary and secondary votages on the same side, I'd expect clearances to be to IEC-60950-1
it very quickly gets confusing. c
Agreed - BS 7671 does NOT apply to pre-manufactured assemblies, which should comply with appropriate standards (Regulation 113.1).
BS EN 62368-1 (IEC 62368-1) supersedes BS EN 60950-1 (IEC 60950-1) and BS EN 60065, both of which are due to be withdrawn this year.
Of course you can fit transformer in a CU. But unless the bellwires at 12 V or whatever coming out are over-sleeved to a standard that can hold off mains, you should really bring the ELV out in mains flex.
Farmboy:
Sparkingchip:
So can a Din rail bell transformer be installed within a consumer unit?
Andy BYou asked the question, which doesn't answer the question, so what's your answer to either question?
F
tattyinengland:
Well consider a motor control centre where voltages of any size may be present. The controls from automation equipment and telemetry are likely to be present and cables carry no volts at all are common monitoring whether a contactor is open or closed for example.
I know some design goes into this to ensure some separation where possible but often it is not possible in an MCC...........- the design of which - I'm no expert, but I think one way to enable this mixture of voltages in the same finger trunking to is ensure that what ever cables are used are rated (insulation is rated) for the highest voltage present.
More Knowledgeable people than me I'm sure will comment on this shortly I'm sure.
Kind Regards
Tatty
davezawadi:
I thought that had been answered, use sheathed 2 core 0.75 flex. I very much doubt that a din rail TX has ever been type tested in a CU, and can see no reason to do so. There are reasonable limits to apply here, read the type testing document and you will see why.