I tested one this week that passed x5 at 16.9ms but failed x1 with >300. When I ramp tested it it tripped at 75mA.
Also, as someone pointed out on another post, If someone mistakenly installed a 100mA (non-delayed) unit instead of a 30mA one - chances are it would pass if only subjected to a 40ms/150mA test - yet it would hardly provide adequate additional protection.
However, the Hager site still says "The x1 test is no longer a requirement but could of course be carried out". I still assert that they are giving potentially dangerous information for the reason I stated above. "Where did they get this from"? is what I'm wondering.
with the note "times five or above"
I don't see anywhere in 7671 where it specifically says the x1 is not required.
AJJewsbury:with the note "times five or above"
Hence the requirement to trip at 5x is no longer a requirement.
I don't see anywhere in 7671 where it specifically says the x1 is not required.
Why would you expect it to? They regs normally only say what is required - not what isn't. If something isn't mentioned the usual deduction is that it isn't a requirement.
- Andy.
First Point:
I don't see that. It says x5 OR above.
And the problem with that is that in theory you could test at 5A or 50A etc. Like I say, Hager have returned to 150mA. OK, the regs are aligning with BS61008 but this is only confusing things. I think this has been a big mistake. Some Hagers that have been set to 250mA are just about making 40ms at 150mA and some are failing at 150mA. This is making the RCD less effective for additional protection as well as causing problems for testing. They've been sent back as faulty.
Second point:
Yes, good point but I still refer to what I had mentioned in my OP about the fact that had I not tested at x1 I would not have found that it was tripping at 75mA when it should be tripping at no more that 30mA. That means that a person could have touched a live conductor with, say, dusty hands and 74mA could be flowing though their heart and not trip.
Whatever the regs say I think they are wrong about testing RCDs. I also thing that it is a mistake in BS61008 to change the current resquired for 40ms trip from 150mA to 250mA
Like I say, the OSG still mentions testing at x1. It also mentions testing RCDs up to 30mA at x5 but does NOT say "or above".
The more current through the body the faster it should trip with the minimum at 30mA which is the principle of testing at both x1 and x5.
I understand what you're saying about the interpretation of the regs and what they are saying but I'm thinking more in the practical terms.
And where the hell has the spell checker button gone?