John Hill TMIET:
This issue came up on the 18th edition course. The testing procedure for rcd's hasn't changed, it's just the requirement to record the 1x IΔn value that has been removed.
On a 30ma device for additional protection you still need to test at 1/2 x IΔn to rule out nuisance tripping, 1x IΔn to confirm normal operation and the 5 x IΔn value is recorded. If for some strange reason the device does not trip out within the required time at 1 x IΔn then it would be recorded as a C2 in the observations and would need to be repaced, regardless of the 5 x value.
John Hill TMIET:
This issue came up on the 18th edition course. The testing procedure for rcd's hasn't changed, it's just the requirement to record the 1x IΔn value that has been removed.
On a 30ma device for additional protection you still need to test at 1/2 x IΔn to rule out nuisance tripping, 1x IΔn to confirm normal operation and the 5 x IΔn value is recorded. If for some strange reason the device does not trip out within the required time at 1 x IΔn then it would be recorded as a C2 in the observations and would need to be repaced, regardless of the 5 x value.