Sparkingchip:
The test results sheets ask for the rating of the RCD IΔn mA and the disconnection time in mS.
That is what you need to record, it is the 5Δn disconnection time test result that you don’t need to record on the certificates.
Andy B
That can't be true if the RCD is used for ADS in most final circuits TT systems where the circuit requires a disconnection time of 0.2 s, and the RCD trip time exceeds 0.2 s - as it doesn't verify ADS. Even if the 1x test is below 0.2 s, it doesn't mean the 2x test or 5x test would pass.
It's also not true where a 10 mA or 30 mA RCD provides Additional Protection, as the required test is "at least 5x".
Therefore, more often than not, the 5x trip time value is required for verification as per BS 7671 requirements.
Sparkingchip:
The test results sheets ask for the rating of the RCD IΔn mA and the disconnection time in mS.
That is what you need to record, it is the 5Δn disconnection time test result that you don’t need to record on the certificates.
Andy B
That can't be true if the RCD is used for ADS in most final circuits TT systems where the circuit requires a disconnection time of 0.2 s, and the RCD trip time exceeds 0.2 s - as it doesn't verify ADS. Even if the 1x test is below 0.2 s, it doesn't mean the 2x test or 5x test would pass.
It's also not true where a 10 mA or 30 mA RCD provides Additional Protection, as the required test is "at least 5x".
Therefore, more often than not, the 5x trip time value is required for verification as per BS 7671 requirements.