Sparkingchip:
If you were required to record the X5 test result it would ask for it. Have a look at section 11 of the IET OSG.
Yes, 11.5 - Additional protection - requires x5 test. QED.
Agreed that where a BS 4293 RCD only provides ADS in TT systems, 11.2 x1 test may be acceptable, but if it provides additional protection, 11.5 applies also.
Following only Section 11.3 would not necessarily verify ADS in TT systems (but would be OK for TN systems) - as I've discussed the x5 test is required because we don't have a x2 test and I'm not (personally) satisfied that passing the x1 test is OK, as I've had x5 with longer trip times than the x1 test.
Section 11.4 is unlikely to apply, as regardless of the debate on whether BS 7288 is accepted in 18th Edition, for the following reasons:
Sparkingchip:
If you were required to record the X5 test result it would ask for it. Have a look at section 11 of the IET OSG.
Yes, 11.5 - Additional protection - requires x5 test. QED.
Agreed that where a BS 4293 RCD only provides ADS in TT systems, 11.2 x1 test may be acceptable, but if it provides additional protection, 11.5 applies also.
Following only Section 11.3 would not necessarily verify ADS in TT systems (but would be OK for TN systems) - as I've discussed the x5 test is required because we don't have a x2 test and I'm not (personally) satisfied that passing the x1 test is OK, as I've had x5 with longer trip times than the x1 test.
Section 11.4 is unlikely to apply, as regardless of the debate on whether BS 7288 is accepted in 18th Edition, for the following reasons: