TT Earth Spike Installation questions

Former Community Member
Former Community Member
I have two outbuildings going up and I am getting myself tied up in knots trying to decide exactly how I going to do it. Bit of background, this is a DIY installation under BC that will be inspected and tested by an electrician appointed by BC. I need to pass on first test as subsequent tests are expensive. I have a number of questions where the experience of the forum members will be helpful.

Q1) cables to the electrode - In selecting a most likely spot where I will get an earth rod into the ground (fairly hard chalk, overlaid with clay type soil) I am getting confused by some of the terms in the OSG. Table 4.2 ( from the 17th, awaiting for 18th) states that I can gor for a little as 2.5mm2. However, when buried, it goes to 4mm2 for mechanical damage protected, 16MM for corrosion protected and 25mm unprotected. What constitutes mechanical and corrosion protection? Does the PVC insulation on single core cable provide corrosion protection? if not, can someone point me at a cable type that has a suitable sheath layer that does? With regards to mechanical protection, I presume I am again looking at cable tiles/concrete sections or steel pipe protection? or given the danger to the person digging is less significant, would a steel flexible conduit suffice? I do appreciate that a cable break would leave a dangerous condition in the outbuilding.

Q2 - Earth rods 1 - I fear I am going to struggle to get the earth resistance down to a good figure, aiming for sub 50 ohms. I am not clear what gives me a better chance, one deep rod or two shallower rods (around 3m apart). Depth may be a real problem into the chalk (peppered with flints!). My soil conditions vary, around one installation, the soil is is fairly rich for about 30cm, then clay mixed with stones for another 30cm down to chalk. The other area is not as good, it doesn't have the soil (well 5cm or so). 

Q3) What is the correct way to connect multiple rods, single cable  CU - Rod1 - Rod2 etc,?

Q4 - Earth rod alternatives - I have two redundant galvanised steel pipes, 1/2 inch that are about 45m long, both are buried at a good depth and completely disconnected at each end. They run in parallel for most of their length and are about 1.5 m apart. Could I use these to supplement my rods? could I just use them without rods? if so, do you think my Inspector/tester will have any issues as long as my Ra is satisfactory. 


Thanks in advance for any advice offered.


Mike
Parents
  • Former Community Member
    0 Former Community Member
    Hello again. This weekend I have got myself a Peaktech 2700 to test my TT earthing proposals. Whilst it appears to be a nice little tester, the instructions were poor and I used some information from Megger to conduct my tests.

    I have a point close to the garage where I can access the redundant pipe and form a good bonding connector using a U bolt clamp. However, one of the limitations of the tester is cable length, I could not be sure I was getting the mid probe outside of the influence of the pipe due it the pipe runs underground, Hence, I extended the pipe over the top of the ground using insulated 10mm2 copper to give me in effect, a different access point from where I could conduct the test. Please see picture below.

    I conducted various tests moving the mid probe and also going out at various angles. I was somewhat limited due to hard surfaces as to direction of test. My results were great, 28 ohms average and all results with 3 ohms until I moved probe much closer the the outer probe where I started to see an increase. Would value your opinion on the way I have conducted the test.

    However, I may have a problem and would appreciate your view. The redundant pipe is cut off as it exits the floor plate in the house porch. It is in contact with the house floor plate. Do I need to break that connection by cutting pipe off prior to entry to the house?
    dddc681ed071bf4be9e2889327eb562e-original-earth-test.png
Reply
  • Former Community Member
    0 Former Community Member
    Hello again. This weekend I have got myself a Peaktech 2700 to test my TT earthing proposals. Whilst it appears to be a nice little tester, the instructions were poor and I used some information from Megger to conduct my tests.

    I have a point close to the garage where I can access the redundant pipe and form a good bonding connector using a U bolt clamp. However, one of the limitations of the tester is cable length, I could not be sure I was getting the mid probe outside of the influence of the pipe due it the pipe runs underground, Hence, I extended the pipe over the top of the ground using insulated 10mm2 copper to give me in effect, a different access point from where I could conduct the test. Please see picture below.

    I conducted various tests moving the mid probe and also going out at various angles. I was somewhat limited due to hard surfaces as to direction of test. My results were great, 28 ohms average and all results with 3 ohms until I moved probe much closer the the outer probe where I started to see an increase. Would value your opinion on the way I have conducted the test.

    However, I may have a problem and would appreciate your view. The redundant pipe is cut off as it exits the floor plate in the house porch. It is in contact with the house floor plate. Do I need to break that connection by cutting pipe off prior to entry to the house?
    dddc681ed071bf4be9e2889327eb562e-original-earth-test.png