This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Line impedance query

Hi 


I am looking at a job where a supply to a replacement CT scanner has to be calculated.


The current scanner is fed by a cable with line impedance 0.06 at source end of the sub panel that feeds it.


The new scanner must have a line impedance no more than 0.06 so basically I can't use the way on the current panel.


The client engineer has said to run from the intake and provide a cable calc to prove the line impedance is OK for the new scanner feed (this is D and B).


I am using AMTECH and was wondering if there was a way to output line impedance or if I need to show a calculation another way?


The client engaged a firm to do line impedance tests, and their report shows values measured between L1-L2, L2-L3 and L1-L3, but looks like they did testing at the sub panel and not at the intake.


This is basically like PSCC right? So I can get PSCC from AMTECH, divide by root 3 and work out impedance from there?


Am I on the right track? Assistance would be much appreciated.


Regards


Anisur
Parents
  • Former Community Member
    0 Former Community Member
    OK - sounds like you have this in hand via the design consultant


    Good luck - and make sure the services penetrations don't prejudice the shielding of the scanner room


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    OK - sounds like you have this in hand via the design consultant


    Good luck - and make sure the services penetrations don't prejudice the shielding of the scanner room


    Regards


    OMS
Children
No Data