This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Line impedance query

Hi 


I am looking at a job where a supply to a replacement CT scanner has to be calculated.


The current scanner is fed by a cable with line impedance 0.06 at source end of the sub panel that feeds it.


The new scanner must have a line impedance no more than 0.06 so basically I can't use the way on the current panel.


The client engineer has said to run from the intake and provide a cable calc to prove the line impedance is OK for the new scanner feed (this is D and B).


I am using AMTECH and was wondering if there was a way to output line impedance or if I need to show a calculation another way?


The client engaged a firm to do line impedance tests, and their report shows values measured between L1-L2, L2-L3 and L1-L3, but looks like they did testing at the sub panel and not at the intake.


This is basically like PSCC right? So I can get PSCC from AMTECH, divide by root 3 and work out impedance from there?


Am I on the right track? Assistance would be much appreciated.


Regards


Anisur
Parents
  • Thanks OMS, all fun and games


    Don't think the guy wants to be involved - sounds like his fee is very small.


    At least the line impedance thing is sorted - I will raise an RFI / proposal to them on the genny bits collating all the bits, as it's getting fragmented
Reply
  • Thanks OMS, all fun and games


    Don't think the guy wants to be involved - sounds like his fee is very small.


    At least the line impedance thing is sorted - I will raise an RFI / proposal to them on the genny bits collating all the bits, as it's getting fragmented
Children
No Data