Ian2304:
Or, does it mean from where the spur connects to the circuit to the point which is the furthest away from the protection device in the consumer unit i.e. a point half way around the circuit beginning from the consumer unit? If so, the maximum length of the spur cable would be longest nearer to the consumer unit and shorter as the furthest point away is reached... Surely this cannot be correct, because at the furthest point the maximum length would be zero - !
That's how I read it. Let's suppose that you have a ring which is 32 m long so the furthest point is at 16 m. You cannot put a spur there. If you put one at the CU, it can be 16/8 = 2 m long; and half way to the furthest point it would be only 1 m max.
A ring serving a kitchen might be only 16 m long, which limits half your possible spurs to 0.5 m, which doesn't seem much use to anybody.
It's only a rule of thumb in a guide. Just ignore it! ??
Ian2304:
Or, does it mean from where the spur connects to the circuit to the point which is the furthest away from the protection device in the consumer unit i.e. a point half way around the circuit beginning from the consumer unit? If so, the maximum length of the spur cable would be longest nearer to the consumer unit and shorter as the furthest point away is reached... Surely this cannot be correct, because at the furthest point the maximum length would be zero - !
That's how I read it. Let's suppose that you have a ring which is 32 m long so the furthest point is at 16 m. You cannot put a spur there. If you put one at the CU, it can be 16/8 = 2 m long; and half way to the furthest point it would be only 1 m max.
A ring serving a kitchen might be only 16 m long, which limits half your possible spurs to 0.5 m, which doesn't seem much use to anybody.
It's only a rule of thumb in a guide. Just ignore it! ??