Or, does it mean from where the spur connects to the circuit to the point which is the furthest away from the protection device in the consumer unit i.e. a point half way around the circuit beginning from the consumer unit? If so, the maximum length of the spur cable would be longest nearer to the consumer unit and shorter as the furthest point away is reached... Surely this cannot be correct, because at the furthest point the maximum length would be zero - !
Ian2304:
Or, does it mean from where the spur connects to the circuit to the point which is the furthest away from the protection device in the consumer unit i.e. a point half way around the circuit beginning from the consumer unit? If so, the maximum length of the spur cable would be longest nearer to the consumer unit and shorter as the furthest point away is reached... Surely this cannot be correct, because at the furthest point the maximum length would be zero - !
That's how I read it. Let's suppose that you have a ring which is 32 m long so the furthest point is at 16 m. You cannot put a spur there. If you put one at the CU, it can be 16/8 = 2 m long; and half way to the furthest point it would be only 1 m max.
A ring serving a kitchen might be only 16 m long, which limits half your possible spurs to 0.5 m, which doesn't seem much use to anybody.
It's only a rule of thumb in a guide. Just ignore it! ??
davezawadi:
This statement is without foundation for practical rings, which are very rarely anywhere near maximum length. As RCD protection is mandatory the Zs question is fairly irrelevant, and voltage drop is just inconvenient and again unlikely to be a problem.
Strangely what regulation does it reference? I suppose none.
I think that the OSG should probably be dumped, it has a number of "old wives tale" comments which are not supported, and any electrician should have a copy of the real regulations, which they should know fairly well (in my experience they don't), and I had a few people turn up for an 18th edition course with just an OSG under their arm! They were really surprised when given a copy of the book to use as to how much was not in the OSG.
I really don't think providing lookup tables that err on the side of caution is responsible for many people being unaware of all of the issues that pertain to the 500 or so pages in BS 7671 (plus all of the attendant standards it references).
I think that's a separate debate all together.
The sentence in 7.2.2 makes no direct reference to the Wiring Regulations, and it is ambiguous.
:
I am not assuming that I am correct, but I am trying to understand.
Would it be true to say that for a radial circuit one equation (more or less) can be used to determine the limits to how that circuit may be used?
Applying the rule of thumb given in 7.2.2, I can install an unfused spur at the consumer unit, not longer than 1/8 the cable length from the spur to the furthest point of the ring, which just happens to be the cable length of the ring i.e. 106m.