AJJewsbury:
The TRT037N appears to be a programmable thermostat - so why the need for an extra channel from a programmer?
What's the motorized valve arrangements? I'm guessing a simple 2-port spring return for the new zone (and similar for the existing zones) - but there are other possibilities that would make things rather different. (I have a long dislike of 3-port valves but some plumbers seem to like them).
I guess you'd also need the microswitch output from the valve to trigger the boiler (in parallel with all the other zones) - which you probably knew anyway, but as you hadn't mentioned it I thought it best to check.
- Andy.
AJJewsbury:
The TRT037N appears to be a programmable thermostat - so why the need for an extra channel from a programmer?
What's the motorized valve arrangements? I'm guessing a simple 2-port spring return for the new zone (and similar for the existing zones) - but there are other possibilities that would make things rather different. (I have a long dislike of 3-port valves but some plumbers seem to like them).
I guess you'd also need the microswitch output from the valve to trigger the boiler (in parallel with all the other zones) - which you probably knew anyway, but as you hadn't mentioned it I thought it best to check.
- Andy.