Q1. According to Guidance Note 7, when installing hot tubs, section 702 should be applied in full. The note to regulation 702.410.3.4.3 recommends that when PME is used, a mat or electrode of 20 ohms or less be connected to the supplementary bonding.
So, if no supplementary bonding is present because there are no extr/exp.c.parts, does an electrode/mat still need to be installed (anywhere on the system)?
Q2. A Matt.e device (https://matt-e.co.uk/single-phase-connection-units/), as used in EV charging to comply with Regulation 722.411.4.1 (iv), of Amd 1, is installed on a tub supply, on a PME system.
So, given it's a hot tub, does the electrode/mat still need to be installed as per the note to regulation 702.410.3.4.3, when:
a) supplementary bonding is present, and,
b) when no exp/extr.c.parts are present, hence no suppl bonding?
(and no, this isn't work I've done).