gkenyon:
ebee:
Well we could all use isolating transformer and configure the ouput as our own TNS just for the chargerUnless I've missed something, I don't think this is any improvement on using TT earthing system just for the charger ... except more expensive?
AJJewsbury:
gkenyon:
ebee:
Well we could all use isolating transformer and configure the ouput as our own TNS just for the chargerUnless I've missed something, I don't think this is any improvement on using TT earthing system just for the charger ... except more expensive?
A transformer would have the advantage of confining any d.c. residual currents to the EVSE system - potentially saving on a lot of expensive B-type RCDs upstream (but we're straying into another thread there),
- Andy.
Sparkingchip:
If you have become an installer and have gained approval to fit specific chargers, how much choice are you going to give potential customers?
Chris Pearson:
Sparkingchip:
If you have become an installer and have gained approval to fit specific chargers, how much choice are you going to give potential customers?So when you go out to buy your EV, how much choice do you get in the M-B dealer, or the BMW one, or the VW one, or ...
The Type B (or Type A or F plus RDC-DD) would still be required for the EVSE.
I don't think there's a requirement (or need) for upstream devices to be anything more onerous than Type A, as the downstream device detects the DC residual current fault. A few manufacturers have been supplying Type A rather than Type AC for a few years now.
John Peckham:
Has any forum member asked for a Declaration of Conformity from EV charging equipment manufacturers and received one?