TT Systems and sprawling construction sites

Hi All


On an open air type construction site in west London (Cross Rail) I have a 100A 3 phase Incommer in a small wooden box at the top edge of site. (nowhere near overheads and not at risk of overheads falling close)


It then goes to metering and onto a 100Amp/0.3 Amp 4 pole RCD in a plastic box (GOOD that its plastic) - its good that its 4 pole. 


There are no client side fuses (This is Bad - south of the meter or after the RCD) and from the RCD it travels 80m in 25mm SWA to a 3 phase DB in a movable metal box on metal legs (So the box provides weatherproofing - as it sits outside in a flower bed essentially. - Its earthed obviously and I am happy with this. No worries.)

The 3 phase DB then goes onto supply three or four metal site cabins and various other kit (For the 10KVa 3 ph 110V transformer the Sole RCD is the 300mA at the origin 80m away which is not good design, but essentially I'm OK with the safety part of it - interestingly there is an 80m run back to the origin for the Tx - 160m round trip - half in 25m 4 core swa to the DB and half in 4mm three core SWA. from the DB - but with a little leniancy on the allowable loadings even volt drop is OK).


All other design criteria seem OK to me through Zs/Ra backed up by the 300mA RCD, thermal constraints vold drop etc. I am installing a new circuit and using the existing SWA - replacing the 110v Single phase Tx for a 3 phase Tx)


With agreement with the clients consultants I have allowed 30Amp three phase for the whole site and no more than 10A Three phase for the Tx 


Now to my question: Do these site cabins need "Bonding" there are two (or 4 perhaps?) ontop of each other and a 5 m gap and then two on top of each other. My feeling is that the B32Amp single phase RCBO supply to each cabin in 3 core SWA will provide earthing via the internal core and another earth path via the SWA armour........What would bonding do? I think - nothing - as there's no zone to keep at equal potential and bonding is not required? 


I've gone through Guidance note 8 and cant see anything like this scenario. 


I think 544.1.1 would only apply to TNS and exporting from a TNS and TT when its a closed building and theres some sort of equipotential zone to protect?


Interestingly I learned by word of mouth - that on railway sites such as this - earth rods are not allowed and only earth mats layed in the ground can be used.............(in place of an earth rod)


These cabins are +/- 10m away from any train overheads and on the other side of a fence between them and the track. 


As you can see I'm tying myself in some knots with this job (But reasonably confident in most things except this bonding/ earthing bit - I'm still definitely learning here)


The metal boxes of the cabin walls will attain internal equal potential anyway hey? 


Lastly a shout out to JP - he has bravely fielded my calls recently and answered questions - free of charge - such as - "can you rely on an S type 300mA RCD supplying a remote sub DB that goes onto supply a B20Amp MCB for a bit of kit (Fibre optic incommer), with no sockets involved on a SWA supply......." -------------It takes a bit of explaining and thank you to him for taking the time. It was the S part of the RCD I was not sure about and that at the origin...so again perhaps not good design but OK. 


I also asked about disconnection times and the part of the table 41.1 (Page 59) under 400V - how I was to achieve that disconnection time of 0.07 when I could not test the 300mA S Type RCD at x 2 or x5 - I did not have the kit for it......Simple mistakes - the Uo = voltage to earth......so I can ignor that bit of the table as all my voltage to earth on this site is 230V. I knew it was 0.2 and 1 second for final and distribution circuits but checked that table and misread  the table wrong. 


So Thank you John for taking some time out to chat.


Kind Regards

Tatty
  • Former Community Member
    0 Former Community Member
    tattyinengland:

    Hi All




    Now to my question: Do these site cabins need "Bonding" there are two (or 4 perhaps?) ontop of each other and a 5 m gap and then two on top of each other. My feeling is that the B32Amp single phase RCBO supply to each cabin in 3 core SWA will provide earthing via the internal core and another earth path via the SWA armour........What would bonding do? I think - nothing - as there's no zone to keep at equal potential and bonding is not required? 


     


    I think you've answered that yourself - what are you actually going to bond to what to create a zone of protection ?


    This is principally the reason that PME isn't used for construction sites - as you can rarely define a zone of protection anyway.


    Regards


    OMS


  • Is there any thought that with TT then an earth rod/plate/mat at each (local) location and bonding/earthing them all together to create one gigantic earth plane are or am I talking utter rubbish? I do almost no TT around here so forgive my ignorance on this one OMS
  • Sorry - I think I forgot to mention that this is a TT system from the origin.
  • Former Community Member
    0 Former Community Member
    ebee:

    Is there any thought that with TT then an earth rod/plate/mat at each (local) location and bonding/earthing them all together to create one gigantic earth plane are or am I talking utter rubbish? I do almost no TT around here so forgive my ignorance on this one OMS


    Generally you want a single earth reference for each system - -so in this case it's all TT and one electrode is all that is required.


    If however, perhaps you decided to run a TN system around, and then crate a TT island of each cabin or group of cabins, then you would ned a separate electrode for each island.


    That said, they can also share the same "ground plane" so linking multiple TT rods wouldn't normally be a problem - provide the whole TT  "electrode" was maintaining social distancing from any TN and particularly any TN-C-S earthing.


    Regards


    OMS