tattyinengland:
Hi All
Now to my question: Do these site cabins need "Bonding" there are two (or 4 perhaps?) ontop of each other and a 5 m gap and then two on top of each other. My feeling is that the B32Amp single phase RCBO supply to each cabin in 3 core SWA will provide earthing via the internal core and another earth path via the SWA armour........What would bonding do? I think - nothing - as there's no zone to keep at equal potential and bonding is not required?
I think you've answered that yourself - what are you actually going to bond to what to create a zone of protection ?
This is principally the reason that PME isn't used for construction sites - as you can rarely define a zone of protection anyway.
OMS
ebee:
Is there any thought that with TT then an earth rod/plate/mat at each (local) location and bonding/earthing them all together to create one gigantic earth plane are or am I talking utter rubbish? I do almost no TT around here so forgive my ignorance on this one OMS
Generally you want a single earth reference for each system - -so in this case it's all TT and one electrode is all that is required.
If however, perhaps you decided to run a TN system around, and then crate a TT island of each cabin or group of cabins, then you would ned a separate electrode for each island.
That said, they can also share the same "ground plane" so linking multiple TT rods wouldn't normally be a problem - provide the whole TT "electrode" was maintaining social distancing from any TN and particularly any TN-C-S earthing.
OMS