tattyinengland:
Hi All
Now to my question: Do these site cabins need "Bonding" there are two (or 4 perhaps?) ontop of each other and a 5 m gap and then two on top of each other. My feeling is that the B32Amp single phase RCBO supply to each cabin in 3 core SWA will provide earthing via the internal core and another earth path via the SWA armour........What would bonding do? I think - nothing - as there's no zone to keep at equal potential and bonding is not required?
I think you've answered that yourself - what are you actually going to bond to what to create a zone of protection ?
This is principally the reason that PME isn't used for construction sites - as you can rarely define a zone of protection anyway.
Regards
OMS
tattyinengland:
Hi All
Now to my question: Do these site cabins need "Bonding" there are two (or 4 perhaps?) ontop of each other and a 5 m gap and then two on top of each other. My feeling is that the B32Amp single phase RCBO supply to each cabin in 3 core SWA will provide earthing via the internal core and another earth path via the SWA armour........What would bonding do? I think - nothing - as there's no zone to keep at equal potential and bonding is not required?