AJJewsbury:
However when I look at table 41.1 it is stating that if Uo is 240Vac the permissible disconnection time is only 0.2 seconds.
The table is based on nominal rather than actual voltage - 230V nominal is usually taken to be anything within the -6% to +10% range - i.e. between 216.2V and 253V. It's very common for DNOs to have far above 230V at their transformers to compensate for voltage drop in the distribution system - typically a 433/250V. So as long as your supply doesn't go above 253V (during times of low load say) I'd say it's acceptable to use the 230V nominal column (e.g. 0.4s for TN small final circuits).
- Andy.
AJJewsbury:
However when I look at table 41.1 it is stating that if Uo is 240Vac the permissible disconnection time is only 0.2 seconds.
The table is based on nominal rather than actual voltage - 230V nominal is usually taken to be anything within the -6% to +10% range - i.e. between 216.2V and 253V. It's very common for DNOs to have far above 230V at their transformers to compensate for voltage drop in the distribution system - typically a 433/250V. So as long as your supply doesn't go above 253V (during times of low load say) I'd say it's acceptable to use the 230V nominal column (e.g. 0.4s for TN small final circuits).
- Andy.