However when I look at table 41.1 it is stating that if Uo is 240Vac the permissible disconnection time is only 0.2 seconds.
AJJewsbury:
However when I look at table 41.1 it is stating that if Uo is 240Vac the permissible disconnection time is only 0.2 seconds.
The table is based on nominal rather than actual voltage - 230V nominal is usually taken to be anything within the -6% to +10% range - i.e. between 216.2V and 253V. It's very common for DNOs to have far above 230V at their transformers to compensate for voltage drop in the distribution system - typically a 433/250V. So as long as your supply doesn't go above 253V (during times of low load say) I'd say it's acceptable to use the 230V nominal column (e.g. 0.4s for TN small final circuits).
- Andy.
lyledunn:
I would agree with Mr Johnson. I would also suggest that if your U0 is not subject to the +10% tolerance then disconnection times as per Table 41.1 can be lifted from the 230v column.
Just out of interest, new Irish Standard 10101 doesn’t bother with the cmin lark.
mapj1:
If it was a curve of disconnection times versus voltage in the regs and not a table no one would care, as 230V and 240v would have times very similar.
But it is not really a sudden step in risk between 230v and 231, more of a gentle rise in risk from quite safe at about 50V to really very bad for you by perhaps 1500V , from which 2 handy values have been converted into safe times for the table.
The origin of the 0.2 secs or 0.4 secs is all about shock currents, and the time it takes to destabilize a human heart. For shocks that last longer than about half a heart beat, a lower current is dangerous, compared to shorter duration events, where we can stand quite a lot more peak current. (we still swear a lot though...)
The assumption on a TN x system is that on fault the appliance will be mid rail between L and E, and the voltages will drop equally along the wiring there and back.
So a barefoot victim gets exposed to about 120V, and maybe we can have an argument about reduced CPC in twin and earth.
For a TT system we assume most of the volt drop is in the earth path, not the live, so the voltage from faulty kit to earth is more like 200V plus, so the maximum safe exposure time is reduced.
For both cases the safe time has to be reduced for 400V, and again by 690, and again by 1200.
Hope this helps.