Mike M:
@gkenyon
Thank you for your response. It can work both ways depending on the fault protective device:
* higher permissible loop impedance using 240Vac in our calculations as per BS7671:2018 clause 411.4.4 (Zs × Ia ≤ U0 × Cmin).
* lower permissible loop impedance due to the fault protective device having to operate more quickly when (Uo) is 240Vac as per BS7671:2018 table 41.1.
Many ABB fuses require more tripping current (Ia) to operate in 0.2 seconds compared to a 0.4 second trip.
What I am gathering is not to take table 41.1 at face value and instead say that a 0.4 second trip time is sufficient for a 240Vac (Uo) circuit ?
Mike M:
@gkenyon
Thank you for your response. It can work both ways depending on the fault protective device:
* higher permissible loop impedance using 240Vac in our calculations as per BS7671:2018 clause 411.4.4 (Zs × Ia ≤ U0 × Cmin).
* lower permissible loop impedance due to the fault protective device having to operate more quickly when (Uo) is 240Vac as per BS7671:2018 table 41.1.
Many ABB fuses require more tripping current (Ia) to operate in 0.2 seconds compared to a 0.4 second trip.
What I am gathering is not to take table 41.1 at face value and instead say that a 0.4 second trip time is sufficient for a 240Vac (Uo) circuit ?