This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Voltage (Uo) for calculating permissible (Zs) earth loop impedance and disconnect times

Former Community Member
Former Community Member
Guys,


Ignoring BS7671:2018 appendix 3 for the purposes of simplifying this discussion.


Private installation, TNCS earthing system where the main transformers taps are set to give phase/phase voltage (U) 416Vac RMS on the secondary side. 


As ye are aware 416V/(√3) = 240Vac RMS line to earth voltage Uo.


I am also being told from an inspector that the permissible disconnection time in table BS7671:2018 41.1 is 0.4 seconds.


However when I look at table 41.1 it is stating that if Uo is 240Vac the permissible disconnection time is only 0.2 seconds.


I am being told by an inspector that we have to use 230Vac when performing permissible earth loop impedance calculations as per BS7671:2018 clause 411.4.4 Zs × Ia ≤ U0 × Cmin.


However if we perform the calculation using 230Vac will will get a reduced permissible Zs. This would seem to suggest to me that we could be failing Zs values that allow enough current to flow in the event of a fault to trip the fault protective device.


Is the inspector wrong ?


Parents
  • There seems to be some confusion about what "nominal" voltage is.


    It is just the number used for calculations.


    230 x 95% = 218.5  If you want to use 240V then Cmin will be 91.04% (ignoring the discrepancy between 218.5 and 216.2V)
Reply
  • There seems to be some confusion about what "nominal" voltage is.


    It is just the number used for calculations.


    230 x 95% = 218.5  If you want to use 240V then Cmin will be 91.04% (ignoring the discrepancy between 218.5 and 216.2V)
Children
No Data