geoffsd:
There seems to be some confusion about what "nominal" voltage is.
It is just the number used for calculations.
Or for the rating of appliances and other electrical equipment, e.g. selection of appropriate semiconductor devices, tests for insulation, etc.
230 x 95% = 218.5 If you want to use 240V then Cmin will be 91.04% (ignoring the discrepancy between 218.5 and 216.2V)
geoffsd:
There seems to be some confusion about what "nominal" voltage is.
It is just the number used for calculations.
Or for the rating of appliances and other electrical equipment, e.g. selection of appropriate semiconductor devices, tests for insulation, etc.
230 x 95% = 218.5 If you want to use 240V then Cmin will be 91.04% (ignoring the discrepancy between 218.5 and 216.2V)