geoffsd:
You are missing the point.
Cmin and/or Cmax values are only required to convert pre-calculated tables and only applicable for the voltage used in those table calculations.
What I am saying is to not use those tables but do your own calculations using the appropriate actual voltage needed for your calculations - whether it be a minimum or maximum voltage depending on what is being considered.
Alan Capon:
If you are working to BS7671, then 400V.
If you are working to manufacturer’s data for your loop impedance values, you need to remember that this may differ between manufacturers. If a different make device is fitted, the calculations may not work.
Regards,
Alan.