Mike M:
@gkenyon
Thank you for your response. It can work both ways depending on the fault protective device:
* higher permissible loop impedance using 240Vac in our calculations as per BS7671:2018 clause 411.4.4 (Zs × Ia ≤ U0 × Cmin).
* lower permissible loop impedance due to the fault protective device having to operate more quickly when (Uo) is 240Vac as per BS7671:2018 table 41.1.
Many ABB fuses require more tripping current (Ia) to operate in 0.2 seconds compared to a 0.4 second trip.
What I am gathering is not to take table 41.1 at face value and instead say that a 0.4 second trip time is sufficient for a 240Vac (Uo) circuit ?
geoffsd:
There seems to be some confusion about what "nominal" voltage is.
It is just the number used for calculations.
Or for the rating of appliances and other electrical equipment, e.g. selection of appropriate semiconductor devices, tests for insulation, etc.
230 x 95% = 218.5 If you want to use 240V then Cmin will be 91.04% (ignoring the discrepancy between 218.5 and 216.2V)
In addition to a voltage factor Cmin, there's a voltage factor Cmax which is 1.1 for supplies in accordance with the ESQCR.
geoffsd:
In addition to a voltage factor Cmin, there's a voltage factor Cmax which is 1.1 for supplies in accordance with the ESQCR.
Yes, but only for the "nominal" voltage of 230V. Using 240V it would be 1.0542.
As far as I am aware the voltage tolerances that you are referencing above stem from 1988 when the European electrical standards body CENELEC agreed on harmonization of low voltage
electricity supplies within Europe as further detailed in BS7671:2018 appendix 2. My understanding is that this applies to public electricity supply systems. Does it also apply to private installations such as we are discussing here?
geoffsd:
You are missing the point.
Cmin and/or Cmax values are only required to convert pre-calculated tables and only applicable for the voltage used in those table calculations.
What I am saying is to not use those tables but do your own calculations using the appropriate actual voltage needed for your calculations - whether it be a minimum or maximum voltage depending on what is being considered.
AJJewsbury:
And before that (for as long as I can remember), it was 240V +/- 6% - i.e. 225.6V to 254.4V - i.e. an even higher upper limit - and we still used 0.4s disconnection times in those days.
True the specification was originally intended for public supplies - but the underlying physics (and physiology) of shock protection would be the same whoever owned the supply so I see no logical reason not to adopt the same approach. The definition of voltage, nominal in part 2 of BS 7671 (especially the NOTE) would also seem to suggest that the same fundamental approach can be taken regardless of supply ownership.
- Andy.