I am reviewing an EICR recently issued for a building with several Distribution Boards feeding sub-Distribution Boards.

I have noted that in some instances, the figure recorded for 'Zs at this board' is significantly less than the Maximum Measured Zs for the circuit recorded on the feeding DB.

e.g. DB FF4 is recorded as being fed from DB FF1.  The feeding circuit to DB FF4 is recorded as having a Maximum measured Zs of 0.4 Ohm, but the 'Zs at this board' for FF4 is recorded as 0.05 Ohm - which is less than the 'Zs at this board' recorded for FF1 (0.08 Ohm) - and which, is in fact, in turn itself less than the 'Maximum measured Zs' for the circuit feeding it.  Can this be true or are there errors in the report?  I thought that cascaded Zs can only get larger due to the added impedance of the feeding circuits? This is not my primary area of expertise, but I am concerned that the EICR is being used to justify the upgrade of several circuits which have passed previous inspections with no problem (hope the resolution of the extracts from the EICR below are sufficient resolution to read)...

248ee514524cf5398885518b2007a96a-huge-image.png


b952bae4d3b1f32d959d675c6ede9a16-huge-image.png
05733e3016557d58306811936bac5e50-huge-image.png


Many thanks if anyone is able to confirm my concerns or otherwise put me straight...
Parents
  • Former Community Member
    0 Former Community Member
    Thanks Chris - since this is not my day job, I was not 100% sure if I had understood correctly what information should be recorded in those boxes - I was sure it should be what was actually installed, but wondered if it might have been what the rated capacity of the DB was (which still would have raised many red flags anyway).  I am glad to have my understanding confirmed that it should record what is actually installed.
Reply
  • Former Community Member
    0 Former Community Member
    Thanks Chris - since this is not my day job, I was not 100% sure if I had understood correctly what information should be recorded in those boxes - I was sure it should be what was actually installed, but wondered if it might have been what the rated capacity of the DB was (which still would have raised many red flags anyway).  I am glad to have my understanding confirmed that it should record what is actually installed.
Children
No Data