Can Zs at DB ever be less than the Zs of the feeding circuit?

Former Community Member
Former Community Member
I am reviewing an EICR recently issued for a building with several Distribution Boards feeding sub-Distribution Boards.

I have noted that in some instances, the figure recorded for 'Zs at this board' is significantly less than the Maximum Measured Zs for the circuit recorded on the feeding DB.

e.g. DB FF4 is recorded as being fed from DB FF1.  The feeding circuit to DB FF4 is recorded as having a Maximum measured Zs of 0.4 Ohm, but the 'Zs at this board' for FF4 is recorded as 0.05 Ohm - which is less than the 'Zs at this board' recorded for FF1 (0.08 Ohm) - and which, is in fact, in turn itself less than the 'Maximum measured Zs' for the circuit feeding it.  Can this be true or are there errors in the report?  I thought that cascaded Zs can only get larger due to the added impedance of the feeding circuits? This is not my primary area of expertise, but I am concerned that the EICR is being used to justify the upgrade of several circuits which have passed previous inspections with no problem (hope the resolution of the extracts from the EICR below are sufficient resolution to read)...

248ee514524cf5398885518b2007a96a-huge-image.png


b952bae4d3b1f32d959d675c6ede9a16-huge-image.png
05733e3016557d58306811936bac5e50-huge-image.png


Many thanks if anyone is able to confirm my concerns or otherwise put me straight...
Parents
  • Peter S3:
    @MHRestorations: that is entirely possible- we note that the Cal date for his test meter was 2 days AFTER the date of the inspection...


    Don't consider that an issue, if you are running checks on your equipment throughout the year the period between calibration can extended for several years.


    I was told to get my testers calibrated after three years as a non-compliance and was muttering about it as I stood at the counter in my wholesalers as I was waiting to be served and drop them off for the calibration. There were comments that you must get them done every year from other electricians, my comment was if you cannot test your own testers and be confident that they are reasonably accurate you should not be out and about doing electrical testing with your meters. 


    If you can test electrical installations then you are capable of running interim tests on your own testers.


    It should also be noted that using the same loop meter to measure in different ways 2-wire Hi, 2-wire Low and 3-wire Low at the same point will give different test results, you may get a different result at a different time with the same tester using the same method and all of them will usually vary from Ze+ R1+R2. Using different loop tester will return a different set of results altogether. The should not be huge differences, but things like having a RCD in circuit can add significantly to the test result.


    I did the inspection and testing course along with the exam twenty odd years ago, digital meters were still relatively new products, my tutor passed comment that older electricians often went into melt down using digital meters. The older electricians would test using an analogue meter starting by twiddling the knob to zero it, then connect it and press test the button which sent the needle across the scale, they would try to look at the needle straight on to avoid parallax then take a reading as it wobbled about a bit, before announcing "That's okay" and writing a test result down.


    Now with digital meters you get a result taken as a sample recorded to two decimal places resulting in electricians going into meltdown reaching for tables, calculators and books to confirm that "it's a good result" when all you really want to know is if the fuse will blow or the trip will trip. So if the maximum Zs for a fuse or trip is 1.1 ohms and you have a test result much lower than that it's job done and time to move onto the next thing, unless you get what is obviously a high reading for a large or short cable, in which case the terminals may need checking or something similar.


    At times loop testing requires a bit of thought as to how and why you ended up with the result you got, also if it is an issue or not.


    There is an old saying "Learn to test, test to learn".


    Andy Betteridge


Reply
  • Peter S3:
    @MHRestorations: that is entirely possible- we note that the Cal date for his test meter was 2 days AFTER the date of the inspection...


    Don't consider that an issue, if you are running checks on your equipment throughout the year the period between calibration can extended for several years.


    I was told to get my testers calibrated after three years as a non-compliance and was muttering about it as I stood at the counter in my wholesalers as I was waiting to be served and drop them off for the calibration. There were comments that you must get them done every year from other electricians, my comment was if you cannot test your own testers and be confident that they are reasonably accurate you should not be out and about doing electrical testing with your meters. 


    If you can test electrical installations then you are capable of running interim tests on your own testers.


    It should also be noted that using the same loop meter to measure in different ways 2-wire Hi, 2-wire Low and 3-wire Low at the same point will give different test results, you may get a different result at a different time with the same tester using the same method and all of them will usually vary from Ze+ R1+R2. Using different loop tester will return a different set of results altogether. The should not be huge differences, but things like having a RCD in circuit can add significantly to the test result.


    I did the inspection and testing course along with the exam twenty odd years ago, digital meters were still relatively new products, my tutor passed comment that older electricians often went into melt down using digital meters. The older electricians would test using an analogue meter starting by twiddling the knob to zero it, then connect it and press test the button which sent the needle across the scale, they would try to look at the needle straight on to avoid parallax then take a reading as it wobbled about a bit, before announcing "That's okay" and writing a test result down.


    Now with digital meters you get a result taken as a sample recorded to two decimal places resulting in electricians going into meltdown reaching for tables, calculators and books to confirm that "it's a good result" when all you really want to know is if the fuse will blow or the trip will trip. So if the maximum Zs for a fuse or trip is 1.1 ohms and you have a test result much lower than that it's job done and time to move onto the next thing, unless you get what is obviously a high reading for a large or short cable, in which case the terminals may need checking or something similar.


    At times loop testing requires a bit of thought as to how and why you ended up with the result you got, also if it is an issue or not.


    There is an old saying "Learn to test, test to learn".