Can Zs at DB ever be less than the Zs of the feeding circuit?

Former Community Member
Former Community Member
I am reviewing an EICR recently issued for a building with several Distribution Boards feeding sub-Distribution Boards.

I have noted that in some instances, the figure recorded for 'Zs at this board' is significantly less than the Maximum Measured Zs for the circuit recorded on the feeding DB.

e.g. DB FF4 is recorded as being fed from DB FF1.  The feeding circuit to DB FF4 is recorded as having a Maximum measured Zs of 0.4 Ohm, but the 'Zs at this board' for FF4 is recorded as 0.05 Ohm - which is less than the 'Zs at this board' recorded for FF1 (0.08 Ohm) - and which, is in fact, in turn itself less than the 'Maximum measured Zs' for the circuit feeding it.  Can this be true or are there errors in the report?  I thought that cascaded Zs can only get larger due to the added impedance of the feeding circuits? This is not my primary area of expertise, but I am concerned that the EICR is being used to justify the upgrade of several circuits which have passed previous inspections with no problem (hope the resolution of the extracts from the EICR below are sufficient resolution to read)...

248ee514524cf5398885518b2007a96a-huge-image.png


b952bae4d3b1f32d959d675c6ede9a16-huge-image.png
05733e3016557d58306811936bac5e50-huge-image.png


Many thanks if anyone is able to confirm my concerns or otherwise put me straight...
Parents
  • Peter S3:

    Which raises the question: what would folks advise should be my next step?  The trustees have no confidence to invite the original contractor to repeat/correct the report, and it does not appear that he is NICEIC approved (I was not involved in his initial selection).  I am considering to ask whether he wishes to retract his report or allow us to submit it for independent review - with potential resulting claim through legal channels.


    I can understand why the Trustees have no confidence in the report.


    I think that the first step should be to make the contractor aware of their dissatisfaction. If he is not a member of any professional body, then clearly there will be no possibility of redress there. Being rather pessimistic, it may be necessary to get a new report and the Trustees can consider whether to seek redress for breach of contract.


    Good luck!


Reply
  • Peter S3:

    Which raises the question: what would folks advise should be my next step?  The trustees have no confidence to invite the original contractor to repeat/correct the report, and it does not appear that he is NICEIC approved (I was not involved in his initial selection).  I am considering to ask whether he wishes to retract his report or allow us to submit it for independent review - with potential resulting claim through legal channels.


    I can understand why the Trustees have no confidence in the report.


    I think that the first step should be to make the contractor aware of their dissatisfaction. If he is not a member of any professional body, then clearly there will be no possibility of redress there. Being rather pessimistic, it may be necessary to get a new report and the Trustees can consider whether to seek redress for breach of contract.


    Good luck!