I wonder does a 40Amp meter behave with a 60A load. It looks like such a meter is in the photo at the top RHS of page 5.
The assessment of maximum demand is onerous using OSG or GN1 and will likely result in pre-install notification in most situations However, the change in 722 to allow MD to be assessed by accounting for load curtailment or reduction by automatic or MANUAL means, leaves the door open for the hard sell. Taken to the extreme you could claim that the EV represented the maximum demand alone as the householder has agreed to sit in the dark while his car charges! Why wait until the DNO gives the nod when you can have your lovely new charge point with the nice blue glow fitted right now!
I wonder does a 40Amp meter behave with a 60A load. It looks like such a meter is in the photo at the top RHS of page 5.
The assessment of maximum demand is onerous using OSG or GN1 and will likely result in pre-install notification in most situations However, the change in 722 to allow MD to be assessed by accounting for load curtailment or reduction by automatic or MANUAL means, leaves the door open for the hard sell. Taken to the extreme you could claim that the EV represented the maximum demand alone as the householder has agreed to sit in the dark while his car charges! Why wait until the DNO gives the nod when you can have your lovely new charge point with the nice blue glow fitted right now!