Working on a project where we are replacing an existing cable serving a DC motor. The motor is 690V and has a current of 1440A. The client has advised that the existing cable is 2 x 2c 300mm2 armoured buried below ground for 130m. Now when looking at the tables in BS7671 the maximum load that a 300mm2 can take is 446A (90C) or 379A (70C) so with the parallel cables this would only provide a current-carrying capacity of 892A ( 758A @70c). We are now concerned that the existing cables installed cira 20 years ago are undersized for the full load current of the motor.
A suggestion was made that we could possibly install single-core armoured cables which would increase the current-carrying capacity. When looking at the tables in BS 7671 (Table 4E3A & Table 4D3A) there are is no data provided for when these cables are in reference method D. I have spoken to a cable manufacturer who pointed me to ERA table 6 but these current-carrying capacities would not be in line with BS7671 as they use different data. I am tempted to use the ERA data as there is no equivalent information in BS7671, Why is this not provided and would there be issues with this.
The client has limited data for the existing installation but they have not had any issues with the current cabling even though it appears undersized. Any help would be appreciated.
regards