UKPN:
I agree with many of these posts, but above all the 18th ed clearly says previous eds are not necessarily unsafe.
That's all well and good. The problem is that the new landlord regs say nothing about requiring the electrical installation to be safe; instead it requires the installation to comply with BS7671:2018 at all times while it is let out.
UKPN:
I agree with many of these posts, but above all the 18th ed clearly says previous eds are not necessarily unsafe. The house I live in is 1974. Cable sheath earth, 0.3, Bonding, supplementary bonding, new switches, sockets. Exis cooker control panel. RCD sw socket by back door for mower etc. Everything tests out. In my opinion the installation is perfectly safe. If I for some reason I had to have an EICR, and the guy said its unsafe by way of a "code" (C2)
I would challenge him. It wouldnt be pleasant, I would want a written explanation as to why.
These nonsensical C2s for 1970/1980s fuseboards, shower without an RCD where the bathroom is bonded throughout. Ifs/mights/maybes/could doesnt cut it with me. "The fuse(MCB) board might catch fire". The fuse board is built to BS????, the board can cope with the PSCC, the terms are tight, the load is in spec, how is it going to catch fire?
Regards, UKPN
I agree with UKPN. I am not rushing to "upgrade" my 1982 installation, but I shall do so when time allows. It won't make me feel any safer.
SPD? They wouldn't need to if pre 18th ed.
UKPN:
SPD? They wouldn't need to if pre 18th ed.
Regards, UKPN
The requirement for domestic lighting circuits to have RCD protection only came in in the 2018 edition of the Wiring Regulations, but you cannot choose not to consider it when undertaking the preparation of an EICR.
Andy B
Chris Pearson:
The real question is: "Is this installation in a satisfactory condition for continued service?" (651.1)
We know that lack of compliance with the current edition does not necessarily mean that an installation is unsafe for continued use (Introduction to BS 7671:2018, page 4).
Bearing in mind that the report is not being prepared for an owner occupier, but for a landlord who has a legal requirement to comply with the new legislation that specifically states a requirement for compliance with BS7671:2018 to ensure the safety of tenants, visitors and contractors who may live, visit or work within the property.
The Housing Health and Safety Rating System (HHSRS) makes interesting reading, presumably no one undertaking a visual only assessment of an electrical installation without testing can be expected to spot everything.
23 ELECTRICAL HAZARDS Include hazards from shock and burns resulting from exposure to electricity but not risks associated with fire caused by deficiencies to the electrical installations, e.g. ignition caused by a short circuit.
This EICR is only part of the process, landlords should be arranging for or carrying out interim visual inspections between the five yearly EICRs.
Andy Betteridge.