Should the unistrut be bonded to the installations metal work. A measurement from the Starter Panel to the metal unistrut reads 0.12megaohms but as the flex is cable tied to it is it a requirement? The flex is ran from a plastic junction box mounted on the unistrut, the flex is ran from the JB to a 110v solinoid approx 1 meter away. Thanks for your help guys.
Andy you’re the man. Thank you. I take it in my case it does not need a connection to earth as it doesn’t present an earth potential. If it did present an earth potential is the easiest way to get this to comply by just linking the earth ring of the gland closest to the unistrut and connecting it to earth that way through the armour of the cable?
Andy you’re the man. Thank you. I take it in my case it does not need a connection to earth as it doesn’t present an earth potential. If it did present an earth potential is the easiest way to get this to comply by just linking the earth ring of the gland closest to the unistrut and connecting it to earth that way through the armour of the cable?