ebee:
Can`t we cheat that one in a similar manner?
At best it will only check the RCD itself is working under those conditions (Fake TNC-S) and not the actual conditions on site but hey ho better than not testing at all methinks
The testing would only be "site conditions" if the unit is tested at the site it's being used at, which won't be the case for many touring caravan periodics (or "service checks"), and pre-delivery or pre-use inspections of mobile and transportable units.
Also, as I said earlier, do we need to worry about the actual cpc being part of the test, particularly considering that
(a) we check earth continuity anyway and
(b) for additional protection, the fault path doesn't necessarily include the cpc.
gkenyon:
Wouldn't this provide electrical separation to more than one item of equipment if used on a caravan or mobile/transportable unit?
I'm not a big fan of that idea, especially as the RCD test will actually introduce a fault ... and I may be in contact with exposed-conductive-parts at the same time ... for example when resetting the RCD in a transportable unit with metal CU !
I think I'd prefer to simply connect the caravan or unit to a socket-outlet with additional protection by 30 mA RCD in accordance with Regulation 411.3.3 or 708.415, and conduct the "up/down" test on the RCD in the caravan or mobile/transportable unit !
Yes, you're right, there is not an easy cheat to avoid dismantling the caravan installation for some testing by at least opening up the consumer unit within the caravan, even for something as simple as testing the RCD inside the caravan with a RCD tester of any type without tripping an upfront site installation RCD.
I have been trying to figure out the wiring arrangement within that Seaward PAT RCD isolation transformer test adapter and ended up back at square one with an CPC to neutral link inside it, the conclusion I came to is that with an isolation transformer is that you don't need RCD protection downstream of it and you have got to tweak the wiring arrangement to reintroduce an "earth" connection to fire the RCD off, so it's no longer an isolation transformer.
Andy Betteridge.
gkenyon:
See Fig A722 in Amendment 1:2020.
That's not in the Big Blue Book, I'll have to have a look online on the IET website, I am guessing we are heading off in the direction of how to use an isolation transformer for charging an electric vehicle.
Andy betteridge.
gkenyon:
See Fig A722 in Amendment 1:2020.
BS7671:2018:Amd1
That's the arrangement I pictured it in my mind to get the RCD to trip under test using an isolation transformer, it takes away risks associated with broken PEN conductors, but surely has to reintroduce some risk, but I suppose an EV is not double insulated like an electric razor and a hell of a lot bigger and there's not much of an option to solely rely on the isolation transformer.
By now we could have took the RCD out of the caravan, bench tested it and put it back in again ?