ebee:
My reluctance to elaborate in open forum was because (ref the N trick) it should done under very careful conditions.
Personally I was envisaging disconnecting the RCD from all local circuits and the local (caravan) earth/metalwork.
That is, a purely 2 wire test with the incomming N linked to earth test lead on the meter (my meter only does 3 wire test).
In other words the equivalent of a "bench test".
Of course the other caution is all other persons would be excluded and I would be the only one about, locked doors etc etc.
Of course MAPJ1s mention of a polarity test prior metered tests is an excellent idea.
Like I said, I did not really want to mention it because if any precautions are missed it is potentially dangerous and I did not want to risk someone becomming startled by their own mortallity.
What's the danger? It's not like we're connecting the installation's exposed metalwork to N - it's only the meter's earth lead that's connected to the supply N. Electrically isn't it similar to many RCD's test buttons - that connect outgoing L to incoming N (or vice versa) via a resistor?
- Andy.
gkenyon:
I do, however, object to the "up/down" method being called an "N trick" - it's a procedure that's recommended in a British Standard Published Document, and in this particular case may well be safer than disabling an upstream RCD
I don't view it as a "trick" it does however require dismantling of the installation and it cannot be done with some portable RCD devices such as plug in RCD adapters. In a BS7909 installation everything should be bench tested before going to site, so a socket without RCD protection at the back of the test bench seems the obvious answer. For several years I have tested some BS7909 distribution boards for an events company, they PAT guy does all the leads etc, but fought shy of doing the distribution boards, so I have the issue of testing RCDs in mobile distribution boards at home, where all my sockets are RCD protected. But not this year, all the events have been cancelled.
Andy B.
Paul Robinson:
I have an acquaintance who asks why his IET 18th Edition RCD tester when plugs it in to the Local RCD
Paul , Swindon LN IET.
From the original post, I was specifically exploring how to do the RCD test by plugging the tester in, rather than dismantling the installation.
The answer is use the test button on the RCD apart from when annual servicing is being carried out, then the cover needs to come off the consumer unit.
Andy Betteridge
Sparkingchip:
I don't view it as a "trick" it does however require dismantling of the installation and it cannot be done with some portable RCD devices such as plug in RCD adapters.
Yes it can be done very safely with PRCDs using plug-in test adaptors, provided there's a socket-outlet at the other end (so, plug-in RCD, or RCD plug on an extension lead).
This technique should also work for testing at double SRCDs where the RCD element is shared between the two outlets ... but of course not for testing the SRCD itself: to test the SRCD you'd have to pop the green wire with a probe on the incoming N.
A double socket-outlet is not always necessary, provided you choose two socket-outlets on the same circuit downstream of any RCD, it won't trip whilst you test the PRCD.
Certainly this gets higher marks from a H&S advisor to the measurement at a CU approach.
From the original post, I was specifically exploring how to do the RCD test by plugging the tester in, rather than dismantling the installation. The answer is use the test button on the RCD apart from when annual servicing is being carried out, then the cover needs to come off the consumer unit.