Connecting two earthing systems - PME on both - any implications of this?

Former Community Member
Former Community Member
Question out of theorotical interest, can you connect the earthing systems of two PME supplies to achieve equipotential bonding between the two electrical supoplies or devices they power?


What are the pro's and con's of this? I understand the implications of PEN faults which might make the earth have touch voltage but if there is equipotential bonding between two earth systems would the earth fault current (earth which now carries live voltage from neutral) not flow through to the earth of the other PME supply?


Appreciate your thoughts.
Parents
  • rather depends if they are on the same substation, and if the fact you are adding a parallel link to the street cable neutral matters.

    The correct advice is 'not unless the DNO say it is OK'. They should know the likely diverted current.  Generally they do not like 2 PME supplies in the same buildingg without a lot of deliberation.