If it exceeds 100A on the phase the mains incoming or service fuse should blow anyway hence preventing any risk to people?
					tattyinengland:
And just to add my 2P.......544.1.1 is for the bonding...........Which I think the OP is asking about - as he says, "to achieve equi potential bonding"
Where an installation has more than 1 source of supply to which PME conditions apply, a main protective bonding conductor shall be selected acording to the largest PEN conductor of the supply.
The same would apply if a TNS and a TNCS supply were in the same building I believe ..........
I've had this before and the a new gas and water supply ended up common to a much larger building and needed to be bonded for the larger PME supply between the smaller supply and the PME supply........ LOOOONG runs of 35mm earth in my case.
There was an interesting article written in wiring matters I believe where the article addressed how long those bonding conductors could be.....
So if we had a few cores of 10mm2 or 25mm2 cable then we could use that to link the earth bars of the two PME supplies in the CU / DB?
My sparky seems to think connecting two earth supplies is very risky and does not even want to have that discussion with the DNO. We got 1x connection through an ICP and the other was historically there through DNO and everything was signed off on both installations.
The ICP provided supply is 3 phase 100A and the existing supply in the building is single phase 80A. If two circuits from the 3 phase (on different phases) to enter a sole room supplied with only the new power supply how would that work with regards to earth bonding?