This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Connecting two earthing systems - PME on both - any implications of this?

Former Community Member
Former Community Member
Question out of theorotical interest, can you connect the earthing systems of two PME supplies to achieve equipotential bonding between the two electrical supoplies or devices they power?


What are the pro's and con's of this? I understand the implications of PEN faults which might make the earth have touch voltage but if there is equipotential bonding between two earth systems would the earth fault current (earth which now carries live voltage from neutral) not flow through to the earth of the other PME supply?


Appreciate your thoughts.
Parents Reply Children
No Data