What do you mean by "the Switchgear"? Do you mean the 'switchgear assembly' (i.e. the switchboard or panel or distribution board,etc.) or do you mean 'the installed circuit breaker'?
A rating of 50kA @ 1s is generally a rating that could be either.
In most contexts I would take it to be the short circuit rating of the assembly (i.e. the busbar rating) but if there is the slightest doubt I would suggest asking the supplier/manufacturer for confirmation.
What do you mean by "the Switchgear"? Do you mean the 'switchgear assembly' (i.e. the switchboard or panel or distribution board,etc.) or do you mean 'the installed circuit breaker'?
A rating of 50kA @ 1s is generally a rating that could be either.
In most contexts I would take it to be the short circuit rating of the assembly (i.e. the busbar rating) but if there is the slightest doubt I would suggest asking the supplier/manufacturer for confirmation.