Short circuit rating of Switchgears - Terms

a410bc3febe07f57b3b7f4e894bd9162-huge-lv-switchear-terms.png
Parents
  • Hi Nick,

    What do you mean by "the Switchgear"? Do you mean the 'switchgear assembly' (i.e. the switchboard or panel or distribution board,etc.) or do you mean 'the installed circuit breaker'?

    A rating of 50kA @ 1s is generally a rating that could be either.

    In most contexts I would take it to be the short circuit rating of the assembly (i.e. the busbar rating) but if there is the slightest doubt I would suggest asking the supplier/manufacturer for confirmation.