Sparkingchip:Connecting a loop tester performed more than one test at the same time.
To be honest when changing a light fitting I will connect the tester to check polarity, loop impedance and then trip the RCD if there is one before taking down the old fitting, then walked back to the consumer unit to isolate, then confirm the fitting is dead and so on and do forth.
Agreed ... but ... Polarity test should be conducted BEFORE energization, see Regulation 643.1
And regards the other situation ... yes, I'm sure we get too many of those.
gkenyon:Sparkingchip:Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Polarity Test can be a dead test, and in that respect is far less dangerous than removing the cover of the consumer unit to conduct live tests.
Connecting a loop tester performed more than one test at the same time.
To be honest when changing a light fitting I will connect the tester to check polarity, loop impedance and then trip the RCD if there is one before taking down the old fitting, then walked back to the consumer unit to isolate, then confirm the fitting is dead and so on and do forth. Bearing in mind there's lots shoddy wiring out there to catch out the unwary, like the Bulgarian builder who dismantled this socket fitting and the bathroom fitter who pulled the cable into the back of it.
Sparkingchip:
From experience I would say two people on a circuit is more dangerous than one, I have seen other electricians working in pairs energise circuits whilst one of them is still working on it, one pair did it three times in one day.
In which case they have not undertaken safe isolation. Lock off with a hasp and one padlock each.
Sparkingchip:Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Polarity Test can be a dead test, and in that respect is far less dangerous than removing the cover of the consumer unit to conduct live tests.
Sparkingchip:
. . . There is a precedent.
https://www.manchestereveningnews.co.uk/news/greater-manchester-news/dads-agony-after-apprentice-electrician-9085985 . . .
There may be a precedent, but as far as I can see, that is not it. The electrocution occurred whilst getting to the point of work, due to the travelling crane not being isolated, not as a result of tests being carried out at the point of work. I am of course assuming that this was an approved method of getting to the place of work.
Regards,
Alan.