MrJack96:
Can someone explain this regulation to me. Is this why we don’t fuse 16amp plug sockets?
The only reason that 13 A UK plugs are fused, is to protect the appliance lead from overload or fault current when the socket-outlet is supplied by a 30 A or 32 A ring final circuit.
When supplied from a circuit protected by a 20 A (or less) fuse or circuit breaker, appliance leads of 0.75 sq mm or larger do not require a fused plug.
This is why other EU countries (in fact most other countries full stop) don't have fused plugs.
lyledunn:
I am not so sure that the plugtop fuse provides overload protection. I would have thought it was there to provide the lead with fault protection. Hence the reason a 0.75mm2 flex can be supplied directly from a 20A PD when it’s Iz is only around 6A.
Agreed. I lost my train of thought part way through and had to come back to the reply - apologies.
The appliance rating itself counts instead of the overload protection.