Regulation 433.3.1

Can someone explain this regulation to me. Is this why we don’t fuse 16amp plug sockets?
Parents
  • MrJack96:

    Can someone explain this regulation to me. Is this why we don’t fuse 16amp plug sockets? 


    The only reason that 13 A UK plugs are fused, is to protect the appliance lead from overload or fault current when the socket-outlet is supplied by a 30 A or 32 A ring final circuit.


    When supplied from a circuit protected by a 20 A (or less) fuse or circuit breaker, appliance leads of 0.75 sq mm or larger do not require a fused plug.


    This is why other EU countries (in fact most other countries full stop) don't have fused plugs.