John Peckham:
Sorry Chris but fairness has never been one of my weaknesses.
IR often creeps up if the IR test button is held down especially if the installation is large as with a good IR the installation acts like a capacitor with the DC from instrument charging the capacitor.
I would never IR test L/L on a periodic as you can never be sure everything electronic has been disconnected and I am not keen on a claim on my insurance.
When doing periodic, and doing IR Testing L-N to E Im happy with 4 meg, and will note that on the test as global test. Just dont have the time or to start stripping the install down, and then, well actually nothing as everything is mnow above 200Meg
John Peckham:
Sorry Chris but fairness has never been one of my weaknesses.
IR often creeps up if the IR test button is held down especially if the installation is large as with a good IR the installation acts like a capacitor with the DC from instrument charging the capacitor.
I would never IR test L/L on a periodic as you can never be sure everything electronic has been disconnected and I am not keen on a claim on my insurance.
When doing periodic, and doing IR Testing L-N to E Im happy with 4 meg, and will note that on the test as global test. Just dont have the time or to start stripping the install down, and then, well actually nothing as everything is mnow above 200Meg