EV socket

Literature from one manufacturer claims that their unit, which is 7Kw single-phase, provides open pen protection in accordance with 722.411.4.1 (iii) but does not require an earth electrode. If the claim is correct, am I missing something? For compliance with that indent,  I thought that the only way it could be done was to provide a measurement electrode unless the unit was three phase.
Parents
  • Hmm, it would be interesting to know how they achieve this claimed reference.


    Top of my head (not a busy place!) I`d guess a 3 phase could detect phase to N are approx balanced voltage?


    .Therefore single phase needs a check to see if around 240 (230) UK
Reply
  • Hmm, it would be interesting to know how they achieve this claimed reference.


    Top of my head (not a busy place!) I`d guess a 3 phase could detect phase to N are approx balanced voltage?


    .Therefore single phase needs a check to see if around 240 (230) UK