EV socket
Literature from one manufacturer claims that their unit, which is 7Kw single-phase, provides open pen protection in accordance with 722.411.4.1 (iii) but does not require an earth electrode. If the claim is correct, am I missing something? For compliance with that indent,  I thought that the only way it could be done was to provide a measurement electrode unless the unit was three phase.
  • Hmm, it would be interesting to know how they achieve this claimed reference.
    Top of my head (not a busy place!) I`d guess a 3 phase could detect phase to N are approx balanced voltage?
    .Therefore single phase needs a check to see if around 240 (230) UK
  • My guess would be that it measures the LE voltage and the NE voltage.  LE should be about 230V and NE should be about 0V.  Anything else suggests a fault - and it doesn't really matter exactly what the fault is.  A completely broken PEN is liable to float at about 115V, especially if there are LE and NE filter capacitors.
  • Simon Barker:
    In a PME installation in of earthing type TN-C-S, and in some PNB systems, N-E voltage will almost always be zero, so measuring N-PE at the charge point a red herring - it will never show you anything.
    The PEN conductor does indeed float about - but not necessarily at 115 V.
    • If the break is on the single-phase cable to the premises, N will approach the supply voltage to Earth.
    • If the break is in a three-phase portion of the network, you can get a voltage from 0 (if all phases downstream of the break are balanced) to above 340 V (yes, that's rms ... to Earth ... and I know this is greater than U0, but that's what reactance does for you)
  • in accordance with 722.411.4.1 (iii) but does not require an earth electrode. If the claim is correct, am I missing something? For compliance with that indent, I thought that the only way it could be done was to provide a measurement electrode unless the unit was three phase.
    AMD1 (2020) introduduced indent (iv) which covers this kind of approach - basically it opens if the L-N voltage is outside the 207 to 253V range - so really they should be claiming compliance with that rather than (iii) these days (or possibly (v) which appears to cover any other approach they haven't yet thought of).
    I does seem to be a slightly flawed approach though - where the single phase supply is derrived from a 3-phase distribution system it's possible in some circumstances for a broken PEN in the 3-phase part to leave the L-N within the acceptable range even though N/PEN/PE is itself at a hazardous voltage above true earth. Hence it's only allowed on single phase installations - on 3-phase ones it's not permitted as the artificial N approach is then practical and far more reliable. Some manufacturers attempt to mitigate the shortcomings by additionally monitoring the current in the EV's c.p.c. and opening if it looks to be approaching 30mA - but whether that might trip over diverted N currents on a PME system if the car bodywork happens to have contact with something connected with true Earth (an open door touching a metal bollard for example) has yet to be seen.
  • AJJewsbury:
    Whilst factually correct, the whole picture is not quite that bleak for the basic 722.411.4.1 (iv) device. In a real open-PEN situation, the Neutral displacement shifts around in phasor space as connected loads change (in some cases, this can also be because those loads have "popped" due to overvoltage, or other loads have disconnected due to undervoltage).
    Any additional monitoring a particular manufacturer could add to the basic picture can only improve safety.
    From an installer's perspective, though, it's worth checking that you install the product at the correct point in the installation for the monitoring voltage, and the lower voltage (207 V) is of more concern. This is the lowest voltage that should be seen at the EV charging point - it's the utilization voltage. If the device is installed upstream of this, at the origin, the lowest voltage that should be seen by the device (trip voltage) is 216.2 V - the lowest supply voltage (in accordance with the ESQCR).
  • gkenyon:
    Simon Barker:
    Quite right.  I was getting confused and thinking of a broken E between the MET and the charger.