EV socket

Literature from one manufacturer claims that their unit, which is 7Kw single-phase, provides open pen protection in accordance with 722.411.4.1 (iii) but does not require an earth electrode. If the claim is correct, am I missing something? For compliance with that indent,  I thought that the only way it could be done was to provide a measurement electrode unless the unit was three phase.
Parents
  • My guess would be that it measures the LE voltage and the NE voltage.  LE should be about 230V and NE should be about 0V.  Anything else suggests a fault - and it doesn't really matter exactly what the fault is.  A completely broken PEN is liable to float at about 115V, especially if there are LE and NE filter capacitors.
Reply
  • My guess would be that it measures the LE voltage and the NE voltage.  LE should be about 230V and NE should be about 0V.  Anything else suggests a fault - and it doesn't really matter exactly what the fault is.  A completely broken PEN is liable to float at about 115V, especially if there are LE and NE filter capacitors.