Simon Barker:
My guess would be that it measures the LE voltage and the NE voltage. LE should be about 230V and NE should be about 0V. Anything else suggests a fault - and it doesn't really matter exactly what the fault is. A completely broken PEN is liable to float at about 115V, especially if there are LE and NE filter capacitors.
In a PME installation in of earthing type TN-C-S, and in some PNB systems, N-E voltage will almost always be zero, so measuring N-PE at the charge point a red herring - it will never show you anything.
The PEN conductor does indeed float about - but not necessarily at 115 V.
Simon Barker:
My guess would be that it measures the LE voltage and the NE voltage. LE should be about 230V and NE should be about 0V. Anything else suggests a fault - and it doesn't really matter exactly what the fault is. A completely broken PEN is liable to float at about 115V, especially if there are LE and NE filter capacitors.
In a PME installation in of earthing type TN-C-S, and in some PNB systems, N-E voltage will almost always be zero, so measuring N-PE at the charge point a red herring - it will never show you anything.
The PEN conductor does indeed float about - but not necessarily at 115 V.