geoffsd:
With RCDs fitted the 200A can be discounted as the current required to operate the RCD is only 30mA, so the impedance can be 1,666 Ohms (50 / 0.03). Were the impedance to be above this 1,666 Ohms then SB would still be required but this is very unlikely.
Yes but the RCD doesn't limit the shock current to 30 mA. What it does do is limit the duration to 40 ms at 150 mA or greater.
geoffsd:
With RCDs fitted the 200A can be discounted as the current required to operate the RCD is only 30mA, so the impedance can be 1,666 Ohms (50 / 0.03). Were the impedance to be above this 1,666 Ohms then SB would still be required but this is very unlikely.
Yes but the RCD doesn't limit the shock current to 30 mA. What it does do is limit the duration to 40 ms at 150 mA or greater.