Extraneous conductive parts

Former Community Member
Former Community Member
Hello,


Thinking about a domestic dwelling with main bonding to incoming water and gas pipes (even though most are plastic nowadays); all the electrical circuits within the dwelling are protected by RCDs; the only extraneous conductive parts to the bathroom being copper water pipes and copper central heating pipes... Why would the copper pipes need to be main bonded one to another close to the bathroom (in an accessible place for testing, like in an airing cupboard)?


Designing an installation which uses the cold water pipe in place of a main bonding cable (having a cross-sectional area which is greater, after all), why would any of the other three pipes need to be main bonded to that cold water pipe, when all of the pipes connect at the boiler any how?! Yes, if you were to cut all of the pipes and to replace them with plastic pipes then you risk introducing an electrical potential into the bathroom should a fault occur, but wouldn’t anyone doing that plumbing be obliged to consider this risk at that time? 


Otherwise, there is no point considering the use of copper pipes to replace main bonding cables. In which case, it would be necessary to bond the pipes one to another just outside the bathroom and run the cable all of the way back to the consumer unit.


I must excuse myself for being indolent and not referring directly to the wiring regulations, which is from where these ideas stem.
Parents
  • The operation of an RCD when an earth fault occurs depends upon all extraneous-conductive-parts being effectively connected to earth via the main bonding conductor

    Not really - the RCD operates (trips) due to an imbalance of L and N currents - and that imbalance would usually return via the c.p.c. - so the bonding of extraneous-conductve-parts doesn't really make a difference to whether the RCD will operate or not (but the Earthing of exposed-conductive-parts does).


    What the RCD (and any other means of ADS) does do is make sure that the voltage on the c.p.c. (e.g. as a result of a L-E fault) doesn't differ from that on the MET by a hazardous amount for a hazardous duration - the main bonding (pretty much) does similarly for extraneous-conductive-parts (limiting the voltage difference from the MET) - so the combined effect is that it should be very unlikely you'd be able to receive a fatal shock between any exposed-conductive-part and any extraneous-conductive-part within the bathroom.


       - Andy.
Reply
  • The operation of an RCD when an earth fault occurs depends upon all extraneous-conductive-parts being effectively connected to earth via the main bonding conductor

    Not really - the RCD operates (trips) due to an imbalance of L and N currents - and that imbalance would usually return via the c.p.c. - so the bonding of extraneous-conductve-parts doesn't really make a difference to whether the RCD will operate or not (but the Earthing of exposed-conductive-parts does).


    What the RCD (and any other means of ADS) does do is make sure that the voltage on the c.p.c. (e.g. as a result of a L-E fault) doesn't differ from that on the MET by a hazardous amount for a hazardous duration - the main bonding (pretty much) does similarly for extraneous-conductive-parts (limiting the voltage difference from the MET) - so the combined effect is that it should be very unlikely you'd be able to receive a fatal shock between any exposed-conductive-part and any extraneous-conductive-part within the bathroom.


       - Andy.