Horace Horace:
The Ze of 0.01 is not helped by the fact that earth from the switchfuse is via the metal trunking, there is no earth cable to speak of. So I cannot disconnect any parallel paths easily.
You don't want to disconnect the parallel paths - you need to know the highest possible PFC.
3.5 kA at the flat equates to a Zs of 0.07 Ω and an R1 + R2 of 0.06 Ω. If CSA of the conductors is 16 mm², that equates to a length of about 25 m. If the real length is significantly different, you need to question the accuracy of the measurements.
Horace Horace:
The Ze of 0.01 is not helped by the fact that earth from the switchfuse is via the metal trunking, there is no earth cable to speak of. So I cannot disconnect any parallel paths easily.
You don't want to disconnect the parallel paths - you need to know the highest possible PFC.
3.5 kA at the flat equates to a Zs of 0.07 Ω and an R1 + R2 of 0.06 Ω. If CSA of the conductors is 16 mm², that equates to a length of about 25 m. If the real length is significantly different, you need to question the accuracy of the measurements.